Group: DynoMotion Message: 4217 From: Michael Rosenfield Date: 3/13/2012
Subject: velocity servo tuning
I have gotten the servos working sort-of, but I can't seem to make sense of the tuning.
To recap, I am using AMC servo amps in velocity-feedback mode, with +/-10V inputs. The encoders are 4000 count/rev, which translates to 20,000 counts/in of table motion.
Can you explain what these plots show?
Is the tuning in Kmotion only supposed to be for short distances? My following error is about 20 at a 100 count move, and about 65 at a 1000 count move. A 4000 count move usually produces about 250 counts, and if I try to do an 8000 count move, the following error is >10000.
Any help you could provide would be greatly appreciated!
Michael
  @@attachment@@
Group: DynoMotion Message: 4218 From: Tom Kerekes Date: 3/13/2012
Subject: Re: velocity servo tuning [4 Attachments]
Hi Michael,
The D Gain of 1650 is set way too high.  Notice the huge spikes in the Output (Green) of 1650 counts?  The full range of the output is +/- 2047 DAC counts so this is nearly a full output spike.  This is because a minimum change of 1 encoder count/sample x 1650 adds 1650 DAC counts to the output.  The DAC and Amplifier will do nonlinear things with those huge swings.
Reduce the D Gain and add a low pass filter (like 2nd order 1000Hz Q=1.4).  You will likely have to reduce the P and I gains to have a stable system.
The redo the tuning of increasing P I D gains to see how it goes.
Group: DynoMotion Message: 4219 From: Michael Rosenfield Date: 3/13/2012
Thanks! I'll try that in the morning.
Michael
Group: DynoMotion Message: 4220 From: Michael Rosenfield Date: 3/14/2012
I did that, and things changed, but I can't see that there is much improvement in following error.
What is the Bode plot telling me?
The time domain plot looks kind of strange.
Michael
Group: DynoMotion Message: 4221 From: Tom Kerekes Date: 3/14/2012
Hi Michael,
That is better but the system appears to have a lot of friction, low bandwidth, and be very sluggish.  You aren't providing much of any information on what sequence you have performed and what the results were.
If you were to zoom in (left mouse click drag) on the first plot right where it starts to move you could probably see this clearly.  The trajectory (blue plot) starts to move causing an error which causes the output (green plot) to increase but the encoder position (red plot) remains still for quite a while before it breaks free and even begins to move.
The same thing can be shown in the Bode Plot Time domain data.  Looking towards the beginning the random blue plot is the commanded trajectory.  This causes the somewhat random output (green plot), but the position (red plot) doesn't move at all.
The output goes above 100 DAC counts (which is ~ 5% of full speed) with no motor movement at all.
You might be able to overcome this by cranking up the gains but it doesn't seem right.
Either the mechanics has lots of friction or binding, or possibly the amplifier isn't configured and tuned properly.
You might go back to testing the amplifier.  If you command 50 or 100 DAC counts does the motor move?  Does it move at a tightly controlled speed?
Also the Integrator I gain seems quite high.  Zero it out and tune P D first for the best performance.  The I term is normally used for correcting small but persistent errors but it looks like it is being used for the bulk of the output.
Group: DynoMotion Message: 4222 From: Michael Rosenfield Date: 3/14/2012
As far as testing the amp - when the system gets a following error, the KFlop shuts the axis down, but outputs about 20mV on the analog output in quesiton. This causes the axis to move slowly but consistently and smoothly. According to my calculations, this is 4 counts. This happens on either axis.
So I'd have to say that 4 counts makes each of the 2 axes move.
The machine is a knee mill, with 5:1 ballscrews. It is heavy, but moves smoothly by hand.
The encoders are 1000 CPR USDigital with differential outputs, attached by toothed belt to the ballscrew drive pulley. The motor pulley is about 1/5 the diameter of the ballscrew pulley (toothed belt, again).
The amps are set to velocity mode, where 10V=2500 rpm at the motor. This translates to about 500 rpm at the encoder. I'm going to verify the amp settings again.
I started with a gain of .5, and started increasing P, D, and I while watching the error plot, and backing things down when I get oscillation.
I guess I really don't know what I'm doing...
I can set the amps for current mode instead of velocity mode - would this be better? The motors already had tachs on them, so I just figured I'd use them.
Does this information help?
Michael
Group: DynoMotion Message: 4223 From: Tom Kerekes Date: 3/14/2012
Hi Michael,
Yes that was useful.  Sounds like it is more like slow amplifier response causing the delay to move rather than just friction.
It is probably better to stick with the velocity mode and tach feedback if the amplifier can be made to do tight velocity control.  There are two reasons for this:  it probably provides more accurate velocity than the limited resolution encoder can and it detects velocity at the motor rather than after the belt.  Please check the settings again as you said.  There is probably a tach feedback gain pot on the amplifier.  Try increasing that.  You basically want to increase it until it starts to go unstable then back it off a bit.
After that if we could get a useful Bode plot it would help understand things.  The previous Bode plots were pretty useless as there was hardly any movement correlated to the command.  If the amplifier tach feedback is turned up, the PD gains increased a bit, and larger Bode plot stimulus we may be able to get useful measurements.
Hang in there :}
Group: DynoMotion Message: 4224 From: Michael Rosenfield Date: 3/14/2012
Ok, I brought up the gain on the amp, and verified that 10v=2500 rpm, and 0=0.
Also found a bit of slack in the encoder belt.
Now what do you make of these plots? I don't see much  change in the frequency domain, even though the position appears to move.
Michael
Group: DynoMotion Message: 4225 From: Michael Rosenfield Date: 3/14/2012
Here is the x  axis. The motion is following the output, but out of phase. What does that mean?
Otherwise, it has low following error - 45 counts max. Lot of noise on the output, though.
Michael
Group: DynoMotion Message: 4226 From: Tom Kerekes Date: 3/15/2012
Subject: Re: velocity servo tuning [3 Attachments]
Hi Michael,
Those are a little better.  I still don't understand what is going on with the system.  Normally the position feedback loop around a velocity servo is pretty easy and stable with simple P gain and no D gain at all (what happens when you try that?).  But in your case you are putting a huge amount of D gain and still have less phase margin than normal.   I'm not sure if I can fully trust the Bode plot because there still isn't much correlated motion, but it is showing very little phase margin at the 0db crossover at ~30Hz.  The huge D gain should be providing lots of +phase so that doesn't make sense to me.  Is it correct that you have belt between the motor and the leadscrew, and then another belt between the lead screw and the encoder??  These may be the cause of the phase lag.
We can try to add additional +phase at 30 Hz with a lead lag compensator.  Set filter #1 to Pole-Zero mode, set N1,N2 to 15HZ and D1,D2 to 60Hz.  You may need to decrease other gains to get a stable system.
(I think the sort of out-of phase stuff is normal.  That is basically saying that when we are too far ahead to drive backwards).
Group: DynoMotion Message: 4227 From: Michael Rosenfield Date: 3/15/2012
The y axis has motor belt to leadscrew, and then another belt from leadscrew to encoder. The x axis has belt from motor to leadscrew, and the encoder is mounted to the leadscrew.
When I have P and no D, I get a significant delay between command and motion, although it is accurate eventually. As I add P to decrease the following error, I have to add D to keep it stable.
I did add a lead lag compensator, with just those values. I didn't reduce the gain, however, so I got oscillation. I'll go back later and try it again with lowered gain.
The axes act quite differently, which I didn't quite expect.
 So the question is - what am I actually trying to accomplish? I assumed I want to tune things so the step input produces a following error less than 20 counts, which is 0.001" So far, I am running around 17 on each axis. I can email more screen captures, if that would help.
Thanks again,
Michael
Group: DynoMotion Message: 4228 From: Tom Kerekes Date: 3/15/2012
Hi Michael,
You actually want to do a "Move" rather than a "Step" (which is probably what you meant).
The goal is to get the accuracies at the speeds and accelerations that you need.
Group: DynoMotion Message: 4229 From: Michael Rosenfield Date: 3/15/2012
I noticed that responses change between 1000 counts, 4000 counts, and 10,000 counts. Is this normal?
Group: DynoMotion Message: 4230 From: Tom Kerekes Date: 3/15/2012
Don't know what you mean?
Group: DynoMotion Message: 4231 From: Michael Rosenfield Date: 3/15/2012
If I tune for no oscillation with a 1000 count move, and then do a 4000 count move, it may or may not oscillate. I got the 4000 count move working, and tried a 10,000 count move, and the following error was so great it shut the axis down.
Is this expected?
Group: DynoMotion Message: 4232 From: Tom Kerekes Date: 3/15/2012
No that isn't normal.  I would need to see a plot.  But the bigger move might be getting up to a higher velocity or higher acceleration that exceeds some limit.  The plot will tell the whole story.
Group: DynoMotion Message: 4233 From: Michael Rosenfield Date: 3/15/2012
Here are the results of putting the lead lag comp in place, and lowering the gain.
What does this tell you?
Looks like I need to get a book on servo theory!
BTW, this is on the x axis, so the encoder is direct drive on the ballscrew.
Michael
Group: DynoMotion Message: 4234 From: Tom Kerekes Date: 3/15/2012
Hi Michael,
That is looking better.  Notice the phase margin is much higher.
In the Bode plot time domain you can see that the encoder is only moving a few counts so there isn't much information being obtained and the encoder resolution becomes an issue making good measurements.  Lower the frequency of the stimulus and increase the Amplitude to get more accurate measurements.
We could probably shoot for higher servo bandwidth.  Increase the P gain.  Theoreticaly this shifts the entire magnitude plot (blue) upward which in turn will shift the 0db crossover point to the right.  Changing P gain should have no effect on the phase plot (green).  We can probably shoot for 60 Hz or higher.  At the same time shift the Lead/Lag compensator to the right so it is geometrically centered on the crossover point because we want the max phase margin at that point.
Then add in a bit of I gain.
Group: DynoMotion Message: 4235 From: Michael Rosenfield Date: 3/15/2012
I'll try this in the morning.
Why is my Bode plot not listing the gain and phase margins as shown in the documentation?
Thanks for all your help, Tom!
Michael
Group: DynoMotion Message: 4236 From: Tom Kerekes Date: 3/15/2012
Hi Michael,
The data is probably too noisy and too low of bandwidth for it to find the crossover.  You might turn off "smoothing" to see how the raw data is.  It is better to use your eye anyway.  There are a lot of issues with Bode Plot measurements because of encoder not being infinitely precise, disturbances, mechanical/electrical non linearities, etc... that result in noise in the measurements.  So you should be suspicious in what it shows.  But it can still provide invaluable clues to what is going on that would be very difficult to see in the time domain.
Group: DynoMotion Message: 4237 From: Michael Rosenfield Date: 3/15/2012
When I turn off the smoothing, the phase looks like a fog of random dots - I couldnt see any pattern to it at all. The magnitude was not too much different, if I recall correctly.
Group: DynoMotion Message: 4240 From: Tom Kerekes Date: 3/16/2012
That was my point
Group: DynoMotion Message: 4241 From: mrosenfield@hotmail.com Date: 3/16/2012
The raw data matches the smootned data pretty well below 800 hz or so.
The lead lag moved the phase margin. The magnitude hasn't changed much, even with increased p gain.
Problem is, now the output is oscillating at a few hundred hz, but the position is stable. What do I do about this? Sometimes it quits, sometimes not.
Michael
Sent from my Verizon Wireless Phone
-----Original message-----
To:
"DynoMotion@yahoogroups.com" <DynoMotion@yahoogroups.com>
Sent:
Fri, Mar 16, 2012 02:07:34 GMT+00:00
Subject:
Re: [DynoMotion] velocity servo tuning
Hi Michael,
Group: DynoMotion Message: 4242 From: Tom Kerekes Date: 3/16/2012
Hi Michael,
You aren't being very decriptive on what you changed and how the results changed.
The oscillation is probably 1 count servo dither.  If you set the "Move" size to zero you can probably plot what is going on.  Did you add I gain?  This is usually what causes servo dither.  A tiny error gets integrated and causes the output to ramp up to overcome friction to make a correction.  When it finally moves it is likely to overshoot - especially in your case where you have belts between the motor and the encoder.  The tachometer feedback with high gain is the most effective way to detect motion at the motor.  This is usually so small it doesn't hurt anything but is annoying.  Deadband is often successful at eliminating it.  It can be used to basically ignore (deadband gain of zero) small errors (deadband range) or correct them less aggressively (ie. deadband gain of 0.1).
Group: DynoMotion Message: 4243 From: Michael Rosenfield Date: 3/16/2012
Sorry, I was away from the machine, and just sent a quick email.
So here is what I did - filters and gain settings.
I have tried changing the gain settings, but the output oscillation remains, although it will quit after a second or so with some gain settings.
If I remove the lead lag filter, this oscillation goes away, but so does the phase margin.
I tried adding some dead band, and it stopped the oscillation after 2 seconds. Sometimes I can get the oscillation to stop by wiggling the handwheel on the axis drive, sometimes not.
Getting closer, I guess....
Michael
Group: DynoMotion Message: 4244 From: Tom Kerekes Date: 3/16/2012
Subject: Re: velocity servo tuning [6 Attachments]
Hi Michael,
You didn't zoom in on the oscillation so we can't see what it looks like as far as how many encoder counts and at what frequency.  We also can't see what the following error is.
You should always be able to get rid of the oscillation with a large dead band, but of course that may be unacceptable.  You didn't state what values you tried and what were the results.
There seems to be a lot of phase margin.  The D Gain term and the lead/lag filter both add phase margin at the expense of other things.  I'm not sure why the need for D gain.  You can also decrease the effect of the lead/lag filter by moving the frequencies closer together.
Do me a favor and set the I Gain to zero as an experiment to see if it stops the oscillations.  It may also require some deadband.  A new feature could be added to switch off the integrator (I Gain) when the errors are small, so I'm curious if this help in this case.
Group: DynoMotion Message: 4245 From: Michael Rosenfield Date: 3/17/2012
Here are some expanded plots.
x 18 fe expand and x 18 expand are the expanded plots of x 18. This has  I = 0 gain, and D of 2. Lots of oscillation
x 18 db has dead band added, and 0.0001 I gain. This stopped the oscillation after a few seconds, but didn't change it.
x 18 nar series I removed the dead band, and narrowed the filter as shown in x 18 filt nar. I also increased the I to 0.001, and the D to 5.
This is the best compromise yet, with little oscillation, and  fe down to 27 peak. The phase margin is reduced.
I have also run 4000 count and 10,000 count moves, and they work well, although the peak fe increases with the greater moves. I assume this is to be expected?
I hope this is making sense.
What would you suggest next?
Michael
Group: DynoMotion Message: 4253 From: Tom Kerekes Date: 3/18/2012
Subject: Re: velocity servo tuning [12 Attachments]
Hi Michael,
This limit cycle oscillation is being difficult :}
BTW you can see some nasty resonances in the system in the 100 and 200 Hz regions probably due to the belts and masses.
If you study the flow diagram below you can see that the D gain term is not affected by the deadband and always has full effect.
Normally this is a good thing as D gain is a form of damping and reduces overshoot and oscillation.  But I think the source of limit cycle oscillation in this case is mainly due to the rate feedback action.  Let's eliminate the D gain and search for a combination of other parameters that may work a bit better.  You will probably need to widen the lead/lag compensator to restore more phase margin due to the loss of the D term.  In general a lead/lag compensator should always perform better than D gain because the lead/lag compensator should provide the same benefit (phase margin) without the undesirable high frequency gain issues.  D Gain is essentially the same as a 1st order Lead/Lag compensator except with the Lag frequency set to infinity.
You also may want to increase the effect of the Low Pass Filter by reducing the cut-off frequency.  This will reduce the size of the "spikes" in the output when the encoder suddenly changes by 1 count.  (Of course a higher resolution encoder would reduce all these problems).  However reducing the cut-off frequency will increasingly reduce phase margin so don't reduce it too far.   Maybe from 1000 Hz to 300 or 500 Hz.
So in summary:
#1 eliminate D term
#2 widen the lead/lag filter
#3 reduce the low pass cut-off frequency
#4 experiment with the P I and deadband settings for the best compromise.
Also as I asked in the previous email try setting I Gain=0 while adjusting the deadband to see if that helps significantly with the limit cycling.
Group: DynoMotion Message: 4257 From: Michael Rosenfield Date: 3/18/2012
Thanks, Tom.
I will try all this and let you know.
Unfortunately, I am space limited on these two encoders; I'm using the max count available from USDigital in this package size.
I did do some experimenting with I=0, but it didn't seem to make much difference.
I'll do some more.
Michael
Group: DynoMotion Message: 4269 From: Michael Rosenfield Date: 3/19/2012
I eliminated the D term.
I can see the 2 peaks at 100 & 200 hz.
The output oscillation is about 200 hz. So I tried adding a notch filter at 100, and 150, and 200. Of course, this starts reducing the phase margin at 40hz, too.
I could see the reduction of these two peaks on the Bode plot, but it didn't change the oscillation during the move.
If I set I = 0.001, and D =0, and play with P gain 10-20, I can get the oscillation to stop after the move stops, but it doesn't change it during the move.
Adding deadband doesn't seem to change the oscillation, either. I get larger FE at rest (ie, after the move command).
Low pass below 800Hz cuts phase margin and doesn't affect oscillation either. If I cut it too much, I get low frequency oscillations in the axis that shake the whole machine.
Is there a rule of thumb for encoder resolution vs desired position error? I have  1000-count encoders, which translates to 20,000 counts/in of table movement. I was shooting for an accuracy of 0.001", so I thought this would allow me a FE of +/-10 counts.
Or am I figuring this wrong?
Michael
Group: DynoMotion Message: 4270 From: Tom Kerekes Date: 3/19/2012
Hi Michael,
see below:
Group: DynoMotion Message: 4271 From: Michael Rosenfield Date: 3/19/2012
Attachments :
I redid the I=0 experiments, and attached the results.
These are all at gain of 20. The  plots labeled 18 were a gain of 19, not a FE of  18.
So, there are P=20 and I,D=0, and then P=20 and I=0.001, with and without deadband. I have also included the filters I'm using (same ones for all) and
some expanded plots to show the noise.
I fiiddled with the lead-lag filter, and this set represents the best I could get. Same for the low pass filter - this seems to be the best.
So the big difference is that adding some I gain stops the output oscillation after the move, but it is still there during the move. Deadband doesn't remove the oscillation after the move, and with I gain,  it doesn't remove it during the move, either.
I can stop the oscillation at rest by wiggling the axis knob manually a bit.
So, what does this show you?
Michael
Group: DynoMotion Message: 4272 From: Michael Rosenfield Date: 3/19/2012
a note on the previous data - it wasn't a step, it was a move.
However, these plots show what happened when I added some feed forward - still some oscillation, but the fe dropped to 6, even on a long move!
I think this is looking pretty good now - what do you think?
Thanks  again,
Michael
Group: DynoMotion Message: 4273 From: Tom Kerekes Date: 3/20/2012
Subject: Re: velocity servo tuning [2 Attachments]
Hi Michael,
Yes that looks pretty good to me.